>"You cannot use the neutral as a substitute for the equipment ground unless it 
>is being re-used for a replacement clothes dryer, range, or oven, and even 
>then, only under a specific set of conditions (NEC 250.140 if you're 
>interested)."

Having a quick look at NEC 250.140, it sets forth four rules under the 
exception, but I was surprised that a fifth rule does not require a single 
receptacle on the branch circuit -- unless it's covered elsewhere.  As written, 
it seems that multiple receptacles can exist on the branch and depending on the 
neutral routing through the remaining receptacles, it may not present a low 
enough impedance back to the serving panel to function as a quasi-grounding 
conductor for an equipment ground even if rule 2 (10 AWG Cu/8 AWG AL) is 
adhered to.  OTOH and as a practical matter, it's common in home installations 
for ranges, cooktops and dryers to be the only device on their serving 240V 
branch circuits.   