On 2/4/2020 9:43 PM, Mark Schoonover wrote:
Actually reviewing the wiring diagram for a standard breaker box and  the
ground wire isn't  attached to a circuit breaker at all.

Right. The green wire goes to the panel's ground bus, which is bonded to the panel enclosure. Neutral is bonded to the equipment enclosure where power enters the premises. Neutral and green are bonded at that point, and ONLY that point.

The function of the "green wire" is to provide a low impedance path to blow the fuse or breaker in the event of a fault that causes the chassis to be hot.