Angel Vilaseca wrote:
> Good mews then! My MOTs are OK.
> 
> Bad news: although no real power is delivered to my house, the power 
> company will bill me for it! :-)
> 
> Thanks for your help, guys!
> 
> Angel Vilaseca HB9SLV
> 

Only if you get charged for kVA, rather than just kW...

The 147 Watts you measured is 'real' power, the Watts part, so you will 
spin the meter by 147 Watts per hour, or 0.147 kWh at what ever your 
rate is.  This was probably due to copper losses in the transformer and 
any other electronics that was associated with the microwave in its off 
state.  Unless you had removed the transformer 1st of course.

The Watt-less element, or reactive power, cannot usually be measured by 
a domestic kWh meter.  Which is why I was a bit surprised that the 1st 
two respondants mentioned it as, without a suitable meter, you can't 
measure it...

If you are on a non-domestic tariff, and I assume this is the same in 
other parts of the world, but no doubt someone will put me right if not, 
you may have an element related to the kVA demand as well as the kWh 
consumed.  The metering system has to be more complicated to do this and 
it's not normally cost effective for domestic supplies.  At least, in 
the UK it isn't.

However, your statement that 'no real power is delivered' is only partly 
the story.  The reason the electricity companies worry about kVA is they 
do have to supply that out of phase component through the supply cables 
and ensure that there are transformers big enough to supply both parts 
of the electricity supply, plus generators supplying VAr (Volt Amps 
reactive) to the grid to support it.  Sometimes they are generating no 
'real' power and just supplying reactive power to support the Grid. 
However, they often do this when on 'hot standby' ready to take up the 
load if demand increases as it takes a long time to run up boilers and 
synchronise a set onto the bars at a large powerstation, so whilst they 
'do nothing' in waiting they will often excite the windings in such a 
way as to generate 'capacitive' VArs.  That's where the current leads 
the voltage, in an inductor current laggs behind the voltage.

The way that industrial companies, who have alot of big motors which are 
often running at poor Power Factors, and hence high demands for kVA, can 
avoid the extra charges is to fit power factor correction capacitors. If 
you think of how you resonate an antenna, you put enough capacitance and 
inductance together to make the radiating element resonate. Inductors 
are the opposite of capacitors, and vice versa, so if you have alot of 
indictors (motors) you put some capacitors next to the incoming supply 
to give the opposite effect and reduce the amount of kVA you demand off 
the system and reduce the size of cable/transformers etc., needed to 
support your supply.  By the same thinking, putting capacitors next to 
the motors means that your cables in the factory can be smaller as well, 
because they only need to be sized for the kW part and a much smaller 
kVA component.

I'm sure all this is available on the internet, or a good electrical 
engineering book.  ;-)

Dave (G0DJA)