Towertalk
[Top] [All Lists]

Grounding tower legs

To: <towertalk@contesting.com>
Subject: Grounding tower legs
From: n3rr@erols.com (Bill Hider)
Date: Wed, 06 Nov 1996 03:05:43 -0800
gpalfe@pclink.com wrote:
> 
> I just finished erecting a Rohn SSV tower.  Rohn supplied the tower with 2
> large ground rods and some bare solid copper wire, number 10 size.  I know
> this is not the recommended wire size to properly ground the tower.
> 
> Does anyone know the recommended wire type and size to ground the 3 legs?
> 
> Thanks, Greg, wa0bnx
> 
> --
> FAQ on WWW:               http://www.contesting.com/towertalkfaq.html
> Submissions:              towertalk@contesting.com
> Administrative requests:  towertalk-REQUEST@contesting.com
> Problems:                 K7LXC@contesting.com
> Sponsored by Akorn Access, Inc & KM9P

According to ANSI/TIA/EIA-222-F, March 29, 1996, The minimum ground is
two 5/8 inch diameter galvanized steel ground rods driven not less than
8 ft into the ground, 180 degrees apart, bonded with a lead of not
smaller than No.6 tinned bare copper connected to the nearest leg or
metal base of the tower.

Additionally, self-supporting towers exceeding 5 feet in base width
shall have one ground rod per leg installed as above.

There are additional grounding requirements for "equipment" on the
tower.  I emphatically suggest tower novices obtain and study this
specification which is available from Global Engineering Documents @
1-800-854-7179 or 303-397-7956.  This document is not free.

I have no relationship with EIA, TIA, ANSI, Global Engineering
Documents, etc.

73!
Bill, N3RR

--
FAQ on WWW:               http://www.contesting.com/towertalkfaq.html
Submissions:              towertalk@contesting.com
Administrative requests:  towertalk-REQUEST@contesting.com
Problems:                 K7LXC@contesting.com
Sponsored by Akorn Access, Inc & KM9P

<Prev in Thread] Current Thread [Next in Thread>