Towertalk
[Top] [All Lists]

Re: [TowerTalk] Grounding of cables to tower?

To: towertalk@contesting.com
Subject: Re: [TowerTalk] Grounding of cables to tower?
From: Jim Brown <jim@audiosystemsgroup.com>
Reply-to: jim@audiosystemsgroup.com
Date: Thu, 19 Oct 2017 09:48:11 -0700
List-post: <mailto:towertalk@contesting.com>
On 10/18/2017 5:41 PM, jimlux wrote:
h, the fine problem of the meaning of words in different contexts - in Electrical Code land - bonding could well be done by the coax shield, with a couple potential problems:

1a) You'd have to make some reasonable case about what a plausible fault current might be - this is the beauty of Class 2 Energy Limited devices (your doorbell)- the maximum fault current is quite low, so almost anything works. If you're running coax to something also supplied by an AC power cord, it's a bit trickier. Probably would depend on the fusing or overcurrent protection of the power supply.

There are two other issues related to power. Code requires that the equipment  ground (green wire) be run with the phase and neutral conductors. First, if the equipment ground for the power system and the phase conductor don't follow the same path, a fault (phase shorted to ground) forms an inductive loop, the impedance of which can delay the operation of the circuit breaker or fuse. Second, if the separately run equipment ground is broken by some failure, the equipment is no longer protected. This is equivalent to what you had noted with  "unplugging the coax."

73, Jim K9YC

_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk
<Prev in Thread] Current Thread [Next in Thread>