AAARG! I hate it when this happens. My table of wire impedances has an 
error. The formula had a decimal point error. Plus the strap inductance 
calculations has the same decimal point error. I found it while trying 
to verify some of Polyphaser's numbers. The conclusions don't change 
much from before, only a little more surprising since the frequencies 
are lower than before.  Here is a revised table and I'll repeat the 
conclusions with the proper numbers.

------------------
Some interesting conclusions can be drawn from this data. For example, 
at 3.3 Hz the impedance of a #4 wire due to its inductance is the same 
as its skin resistance, but the DC resistance still dominates.  At 112 
Hz the impedance due to inductance is equal to the total DC 
resistance(skin plus DC resistance). That means for any frequency above 
112 Hz, the impedance of the wire is due primarily to its inductance, 
not its DC resistance or skin resistance. As a matter of fact, above 
about 2 kHz, the DC resistance and skin resistances are insignificant 
for this wire, even though they are continually increasing. Since all 
these parameters are linear with length, this conclusion is the same 
regardless of the length of the wire. For a #2 wire, this same point 
happens at 73 HZ instead of 112 Hz.


Calculated data:
#4 wire, 10 ft length, L = 4.13 uH (straight wire in free space)
Note: A wire in the ground will appear as a higher inductance than shown 
here, because of the decreased velocity factor of the medium.
Z(L) represents impedance calculated from inductance only.

Freq       Z(L)       DC res    Skin res
3.3 Hz    8.9e-5     2.49e-3    8.9e-5
93 Hz     2.49e-3    2.49e-3    4.7e-4
112 Hz    3e-3       2.49e-3    5.16e-4
1 kHz     0.027      2.49e-3    1.15e-3
10 kHz    0.269      2.49e-3    4.88e-3
100 kHz   2.69       2.49e-3    1.54e-2
1 MHz     26.9       2.49e-3    4.88e-2

I didn't have a spreadsheet already made up to calculate the skin 
resistance of a strap, but I do have one to calculate its inductance. 
Since the inductance is the predominate parameter, it's probable all you 
will need anyway. The calculations are for a strap thickness of 0.05 
inches, and a length of 10 ft.  Since the thickness doesn't effect the
inductance very much, it wasn't included as a variable parameter. 
Compare these numbers to a #4 wire, same length, which was 4.13 uH.

Strap width   Inductance uH
 0.5 in          3.96
 1 in            3.59
 2 in            3.2
 3 in            2.97
 4 in            2.8
 5 in            2.66
 6 in            2.56

The formula for the wire inductance and strap inductance came from the
Polyphaser book, Grounds for Lightning & EMP Protection.

Jerry, K4SAV

K4SAV wrote:

>All this grounding talk has got me thinking again.
>
>Most of us know that the impedance of a wire is increased by its skin 
>resistance, and that a wire with more skin area (such as a strap) will 
>provide a lower impedance. But how much lower? I decided to break out my 
>spread sheet I made for calculating these things and take a look. The 
>data is tabulated below.
>
>Some interesting conclusions can be drawn from this data. For example, 
>at 330 HZ the impedance of a #4 wire due to its inductance is the same 
>as its skin resistance, but the DC resistance still dominates.  At 1660 
>Hz the impedance due to inductance is equal to the total DC resistance 
>(skin plus DC resistance). That means for any frequency above 1660 Hz, 
>the impedance of the wire is due primarily to its inductance, not its DC 
>resistance or skin resistance. As a matter of fact, above about 20 KHz, 
>the DC resistance and skin resistances are insignificant for this wire, 
>even though they are continually increasing. Since all these parameters 
>are linear with length, this conclusion is the same regardless of the 
>length of the wire. For a #2 wire, this same point happens at 1100 HZ 
>instead of 1660 Hz.
>
>Note that when applying these conclusions to other things besides ground 
>wires, there is a difference between impedance due to inductance and 
>impedance due to resistance.
>
>---------------------
>Calculated data:
>#4 wire, 10 ft length, L = 0.43 uH (straight wire in free space)
>Note: A wire in the ground will appear as a higher inductance than shown 
>here, because of the decreased velocity factor of the medium.
>Z(L) represents impedance calculated from inductance only.
>
>Freq       Z(L)       DC res    Skin res
>330 Hz    8.86e-4    2.49e-3    8.86e-4
>920 Hz    2.47e-3    2.49e-3    1.48e-3
>1660 Hz   4.46e-3    2.49e-3    1.99e-3
>10 kHz    2.69e-2    2.49e-3    4.88e-3
>100 kHz   0.269      2.49e-3    1.54e-2
>1 MHz     2.69       2.49e-3    4.88e-2
>
>
>I didn't have a spreadsheet already made up to calculate the skin 
>resistance of a strap, but I do have one to calculate its inductance. 
>Since the inductance is the predominate parameter, it's probable all you 
>will need anyway. The calculations are for a strap thickness of 0.05 
>inches, and a length of 10 ft.  Since the thickness doesn't effect the 
>inductance very much, it wasn't included as a variable parameter. 
>Compare these numbers to a #4 wire, same length, which was 0.43 uH.
>
>Strap width   Inductance uH
> 0.5 in          0.40
> 1 in            0.36
> 2 in            0.32
> 3 in            0.30
> 4 in            0.28
> 5 in            0.27
> 6 in            0.26
>
>The formula for the wire inductance and strap inductance came from the 
>Polyphaser book, Grounds for Lightning & EMP Protection.
> 
>One other note of significance: None of these calculations include 
>resonant effects. For  wires that are long compared to the frequencies 
>being considered, resonance effects can increase the impedance by a huge 
>amount compared to an impedance value calculated from wire inductance.
>
>Jerry, K4SAV
>_______________________________________________
>
>
>
>_______________________________________________
>TowerTalk mailing list
>TowerTalk@contesting.com
>http://lists.contesting.com/mailman/listinfo/towertalk
>
>  
>
_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>