BUT note that this '"Bonding connection" between the green wire blocks 
and the neutral blocks' is removable and *must be* removed if the panel 
is used as a subpanel -- again, so that the only connection between 
neutral and ground is at the service entrance (which may not be where 
the panel is: e.g., our main breakers -- and one breaker for the garage 
circuits -- are in the garage, back to back with the meter, while the 
panel with all the other breakers -- technically a subpanel -- is in the 
basement).

Alan NV8A


On 10/07/05 03:03 pm Bill Aycock tossed the following ingredients into 
the ever-growing pot of cybersoup:

> No- no added wire. The "metallic conductor" I refer to IS the neutral 
> wire, but there is an added bond from that to the earth ground rod 
> within the panel.
> Significantly, ALL panels I have ever seen have this "Bonding 
> connection" between the green wire blocks and the neutral blocks. 
> Neither the green or the neutral is switched.
_______________________________________________

See: http://www.mscomputer.com  for "Self Supporting Towers", "Wireless Weather 
Stations", and lot's more.  Call Toll Free, 1-800-333-9041 with any questions 
and ask for Sherman, W2FLA.

_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>