RFI
[Top] [All Lists]

Re: [RFI] Power Line Noise

To: rfi@contesting.com
Subject: Re: [RFI] Power Line Noise
From: K9MA <k9ma@sdellington.us>
Date: Thu, 16 Apr 2020 22:50:32 -0500
List-post: <mailto:rfi@contesting.com>
In many cases, I think the current causing noise to radiate is flowing in only one of the lines. For example, if a lightning arrestor were arcing (very common), the current flows primarily in the one line it's connected to and the ground wire. In the horizontal line, the current flows about equally in both directions, so the far field largely cancels.

Another case I've seen often is arcing between a couple poorly bonded pieces of hardware not directly connected to a power line. That current is mostly capacitively coupled from an overhead HV line, flows through the hardware, and either to a ground wire or is capacitively coupled to ground or another line. If the ground wire is involved, the polarization is likely to be mostly vertical. If between lines, perhaps mostly horizontal. In that case, the wide spacing would certainly allow lots of radiation.

I believe near field for antennas is generally considered to be about 1/6 of a wavelength. That's only 11 feet on 20 meters.

Another observation that may prove useful: Poorly bonded hardware near a single phase line is much more likely to be problematic than that near three phase sets, unless it's much closer to one of the phase lines. At any distance large compared to their spacing, the 60 Hz (or 50) fields from the lines mostly cancel, so there's just less field to cause arcing. (Discovered the hard way.)

73,
Scott K9MA




On 4/16/2020 22:30, Jim Brown wrote:
On 4/16/2020 2:32 PM, K9MA wrote:
The current from an arcing device like a lightning arrestor flows in BOTH directions away from the source on the horizontal lines, so the horizontal component largely cancels out. It's like the top of a "T" antenna.

I'd buy that if the wires were close together, but NOT at the wide spacing typical of HV lines. Think about it -- twisted pair is FAR better (20-30dB) than "zip cord" at rejecting all forms of crosstalk and coupling, simply because interfering fields are close to one conductor than the other. That's a fairly small differential, but the two conductors in the AC distro system have far greater spacing. They're also typically 3-phase.

The radiation then mostly comes from the vertical ground wire.

I'm good with this (and I've seen it), but for a different reason -- it can be carrying the arcing of both conductors, perhaps from GFCIs?

Generally, I've found the HF beam heading to be pretty accurate for more distant sources, perhaps because the vertical component is attenuated more quickly.

I agree with Mike that antenna arrays develop their directivity in the far field, and can be VERY different in the near field. Polarization of the RX antenna might be part of it.

 With the VHF tracker (135 MHz), I do find I have to
sometimes turn it vertically, but not consistently up close. I expect the shorter wavelength has something to do with that.

In any case, the moral of the story is don't just look in the direction your HF beam thinks it's coming from!

I'm not suggesting that anyone in this thread might be making this mistake, BUT -- remember that antenna arrays are all based on spacing, phase relationships, and spatial relationships between elements as ELECTRICAL length. A tri-bander only exhibits it's design directivity on those three bands. Its directivity on any other band, including 2M, should be thought of as "random," like the infinite number of monkeys and typewriters. :)

73, Jim K9YC



_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi


--
Scott  K9MA

k9ma@sdellington.us

_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi
<Prev in Thread] Current Thread [Next in Thread>