> On Sat, 2006-09-23 at 11:09 -0600, Ron wrote:
>> Ed,
>> Not knowing all the particulars of the circuit feeding into your shack my
>> suggestion may not be relevant, but here goes anyway. If your 110 VAC 3
>> wire circuit in the shack is dedicated to that location (as in it does
>> not
>> serve other outlets prior to entering the shack), you should be able to
>> install a 220 VAC circuit breaker of appropriate amp rating for the wire
>> gauge at the panel and feed the circuit to the shack from this new
>> breaker
>> giving you 220 VAC to the shack. Install a new sub panel in the shack
>> and
>> provide an earth ground for the new sub panel and split off 220 and 110
>> VAC
>> circuits in your shack from this source. Once you have this installed,
>> you
>> can use the 220 VAC amps. Surface runs of EMT are cheap and quick to
>> install. This improvement may require an electrical inspection and permit
>> from the local building code folks.
>> Ron
>> KA7U
>>
> This will not pass inspection. You are trying to supply a subpanel that
> requires a 4 wire cable with a three wire cable. The addition of a local
> ground rod does not meet the code requirements, nor is running the
> neutral in the bare conductor in the romex allowed by the code. Nor is
> running 120 volts on the white conductor.
>
> It will work but with much reduced shock safety. Don't do it.
> --
> 73, Jerry, K0CQ,
> All content copyright Dr. Gerald N. Johnson, electrical engineer
>
> _______________________________________________
> TenTec mailing list
> TenTec@contesting.com
> http://lists.contesting.com/mailman/listinfo/tentec
>
_______________________________________________
TenTec mailing list
TenTec@contesting.com
http://lists.contesting.com/mailman/listinfo/tentec
|