 I
heard that lightning does not like to take sharp turns, hence, the arc of copper and not bolting to the leg bolt.


Lightning doesn't care - the inductance of a gentle bend or a sharp 90 degree corner or a 45 degree "cut the diagonal" is basically the same - until you start getting a complete turn or more, inductance is all about the length of the conductor.

The rationale behind the "no sharp bends" dictum is to reduce the incidence of flashover from the lightning conductor to neighboring stuff. This is a big deal if you're running a downlead from a lightning rod (air terminal) next to a metal downspout, for instance. You don't want lightning flashing over from the downlead to pipes inside the wall or anything else.

The sharp bend has a smaller radius of curvature, so the breakdown voltage to adjacent objects is less.

Remember that parallel currents cause conductors to be forced together. So your conductor that is bowed out and away, and basically in parallel with the current carried through the base and concrete, is going to be pulled in towards the tower to try and minimize the gap.