Some data from Concrete Society:

"Moist concrete behaves as an electrolyte with resistivity of up to 100 ohm-m. Air dried concrete has a resistivity in the order of 10 000 ohm-m, whilst oven-dry concrete has a resistivity in the order of 100 000 000 ohm-m." So isn't likely that wet concrete is so conductive the energy dissipated is low and dry concrete is so dry it can't make steam or conduct much current? Also consider that concrete is sufficiently conductive that NEC now requires all residential AC outlets over bare concrete floors to be GFI protected.

As a composite material then consider how the rebar matrix reduces the point to point conductivity much more. (I'll leave it to others to figure that out). Then consider how much area is in a Ufer foundation in contact with earth. In my case, about 250 sq ft for a tower base and 720 sq ft for a foundation. Both are wet year round. Compare to a 10' 5/8" ground rod at 1.6 sq ft of area. So the relative current density at the earth interface is 2+ orders of magnitude less for my tower base, assuming the current is uniformly distributed by the rebar matrix (which it isn't since rebar has inductance, but there is a lot in parallel).

I think one idea of a Ufer is to distribute (20' minimum length buried conductor) over enough volume in contact with the rebar so as to prevent very high current densities. Codes or policies that require Ufer's (grounded rebar) for power plants (IEEE), ammunition bunkers (DOD), and explosive storage (ATF) facilities (& NFPA) were convincing to me of the robustness of the engineering. see http://www.wbdg.org/FFC/DOD/UFC/ufc_4_420_01_2015.pdf as a publicly available spec. Some interesting requirements are specified. Bond everything together.

So, I'm also a skeptic about exploding concrete being common or a problem to worry about. I'd like to see a forensic analysis of fractured concrete that proved lightning was the cause, rather than salt water corrosion or improper grounding/construction or urban myth.

Grant KZ1W


On 6/26/2017 11:31 AM, Patrick Greenlee wrote:
There seems to be an urban myth in popular circulation about foundations being subject to being blown to bits or at least cracked open sufficiently for them to fail due to lightning. If this were a real threat wouldn't it be common experience with Ufer grounds? Can anyone provide a reference to a properly documented incident where lightning blew apart a foundation?

I'd be happy to abandon my current thinking and get on board with the lightning blows up concrete folks it there were sufficient factual evidence.

Patrick        NJ5G


On 6/26/17 11:23 AM, Clif Keely via TowerTalk wrote:
Reading through some of the comments here recently have me trying to recall some of the comments I have read over the years. I seem to recall several that spoke to using 2 or 3 ground rods on a tower which might not be a bad idea. I should think one of the reasons would be to keep the discharge energy from making steam within the concrete base and that explosive burst of steam, producing a lot of cracking within the block and with that reducing it's ability as a solid base. I have no research to support this but offer it only as a thought. For myself if I hear thunder I disconnect antenna and power cables. After that I keep my fingers crossed as I think lightning will do what ever it bloody well wishes.
_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk


_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>