Towertalk
[Top] [All Lists]

Re: [TowerTalk] Lightning protection - length of grounding rodsruns from

To: towertalk@contesting.com
Subject: Re: [TowerTalk] Lightning protection - length of grounding rodsruns from tower?
From: Jim Lux <jimlux@earthlink.net>
Date: Thu, 29 Jan 2015 06:35:34 -0800
List-post: <towertalk@contesting.com">mailto:towertalk@contesting.com>
On 1/29/15 5:51 AM, Larry wrote:
The Polyphaser book recommended ground rods spaced at 2x the length of
the ground rods. The purpose was to spread the charge out in the event
of a hit. So is that theory or explanation now out, disproved, or ...?

It has been a long time since I looked at the book so I may not have
remembered it correctly.


Yes.. rods spaced closer than 2x the length are less effective (the limiting case is if you drive the two rods right next to each other.. then it's basically one rod). Once you're 2xlength apart, spreading them further doesn't reduce the impedance much.

Off hand, I think that driving rods close to the concrete doesn't do a heck of a lot of good: you've already got a good connection to a large area of soil.

A good rule of thumb is to imagine the rod as having a "(hemi)sphere of influence" with radius equal to the depth.

If you have a big block of concrete that is 8x8x8 feet, it too has a "sphere of influence" (or more a "blob") that extends out quite some distance. How far? You'd have to do some modeling to figure it out.

But I'll bet there's very little to gain by driving a rod within 20 feet of a Ufer ground

Note that I'm using "sphere of influence" as a visualization concept.. there is no hard cutoff.. the current density gradually decreases.



_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>