On Fri,9/12/2014 6:50 PM, Gary Schafer wrote:
If you have only a 3 wire feed system from your house to garage then you
have to have that feed neutral wire bonded to the panel at both the house
and at the garage. If you do not have it bonded to the panel at the garage
then there is no path for a breaker to trip if there should be a fault of
hot to ground on any appliance like Bill described.

How many times must I say it? Neutral MUST BE bonded in both buildings if ground is not carried. They are treated as separate premises.

73, Jim K9YC