Re: [Amps] 130 V MOV placement ??

To: amps@contesting.com
Subject: Re: [Amps] 130 V MOV placement ??
From: Jim Brown <jim@audiosystemsgroup.com>
Reply-to: jim@audiosystemsgroup.com
Date: Sat, 22 Sep 2018 12:20:00 -0700
List-post: <mailto:amps@contesting.com>
Hi Jim,

WHERE are you placing MOVs?  The only GOOD place for them is at the service entrance, or in the panel where Neutral is bonded to Green. MOVs should NEVER be used on branch circuits distant from the panel.  When MOVs are at a distance from the panel, the strike current raises the voltage of the chassis by virtue of IR drop to the panel. When equipment "protected" by MOVs at different  locations, the strike will put each at a different potential by virtue of the resistance and inductance of the green wire at the two locations. When equipment at these different locations is interconnected, the potential difference between them will fry circuitry.  It is VERY common for computers connected via Ethernet to lose circuitry from a strike.

A good MOV at the service entrance will short strikes incoming on the AC line, but additional current can be induced on branch circuit wiring. To protect against this current frying interconnected equipment, SERIES MODE protectors are required. They absorb the strike in a very large inductor, then release it slowiy after the strike. This type of protector is mfd by SurgeX, Brick Wall, and another mfr whose name I've forgotten. SurgeX has been widely used in pro audio systems for nearly 20 years.

I'm using a Joslyn "whole house" MOV unit at my service entrance, and SurgeX boxes at branch circuits in the shack, my XYL's office computer, my entertainment center (TV, stereo), and for my XYL's computer-controlled sewing machines and looms. That may be overkill -- the only stuff that is interconnected or bonded to ground locally is in my shack and that entertainment center. The Joslyn is hanging across the line through breakers within a disconnect panel.

73, Jim K9YC




On 9/21/2018 12:23 PM, Jim Thomson wrote:
IF  using a 130 V rated   MOV,   where  does it get wired ?   Do you wire 
between  120 vac  and neutral.... or  120 vac and chassis of  equipment in  
question ?

IF  a spike  / transient /  glitch  etc  occurs.and  MOV  conducts..which  path 
do you want the fault current to flow through, the ground wire or the  neutral ?

The only place the  neutral and ground are bonded together is at the main 200A 
panel.   On my 100 A  sub panel, the neutral + ground are NOT bonded,  per the 
electrical code.

Either way, the  MOV  is fused, so if it does fail  shorted... the fuse opens 
up.   Also  I use a neon  /  led  wired between output of fuse..which is also 
the input to the MOV...and neutral.
In normal operation, the  neon / led is illuminated.    IF fuse opens  up, the  
neon / led  goes  out.... telling me the MOV is doa.

Tnx... Jim   VE7RF