On Oct 14, 2005, at 6:44 AM, Carcia, Francis A HS wrote:
> #12 will get pretty warm at 29 amps.
In a conduit, yes. In open air no. For a C-filter supply, wire temp
is not the issue.
>
> -----Original Message-----
> From: Gudguyham@aol.com [mailto:Gudguyham@aol.com]
> Sent: Friday, October 14, 2005 9:40 AM
> To: amps080605@w4zt.com; n5ito@davidv.net
> Cc: amps@contesting.com
> Subject: Re: [Amps] Dedicated 220AC Wiring for Amps..
>
> In a message dated 10/13/2005 7:44:04 PM Eastern Daylight Time,
> amps080605@w4zt.com writes:
>
> Dave,
>
> Below you said you were running 4 breakers, each 30 amps. Then you
> said
> two of those breakers would be wired with #12 wire. If your breaker
> is
> going to be a 30 amp breaker, you must, for safety's sake and to meet
> NEC, use at least #10 wire. You should NEVER use wire rated less than
> the capacity of the breaker. If you are using #12 wire, the breaker
> should never be larger than 20 amps. The length of the run is of no
> consideration when it comes to meeting the minimum requirement of the
> code.
> This is NOT entirely true. If you are running motor circuits you may
> up the
>
> rating of the circuit breaker well over the size wire that is being
> used.
> However, for branch circuits the above is true, but as I have stated,
> NOT
> always.
>
>
>
>
> _______________________________________________
> Amps mailing list
> Amps@contesting.com
> http://lists.contesting.com/mailman/listinfo/amps
> _______________________________________________
> Amps mailing list
> Amps@contesting.com
> http://lists.contesting.com/mailman/listinfo/amps
>
>
Richard L. Measures, AG6K, 805.386.3734. www.somis.org
_______________________________________________
Amps mailing list
Amps@contesting.com
http://lists.contesting.com/mailman/listinfo/amps
|