>> >30A x 100' run on #10AWG CU = 6.9 volts dropped.
>>
>> This is for a resistive load. C filter DC supplies are different. The
>> peak to avg current ratio is c. 10 to 1
>
>Rich, wouldn't this only be applicable during the initial inrush of current
>at power-up
It was recurrent. The transformer had a primary resistance of
0.079-ohms. It used a bar-stock primary winding. The mains R measured
0.075-ohms. We are talking about some serious amperes.
> and that a step-start circuit should limit the inrush of current
>"somewhere close" to that of a resistive load? Or, is the C-input effect on
>AC current seen on full-power CW mode for instance, where the current demand
>rapidly changes with the activation of the key?
>
the peaks were there on SSB. My wife said she could almost make out what
I was saying due to the vibration of the #4 Cu in the attic. My guess
is that peaks exceeded 300A.
cheers, Paul
- Rich..., 805.386.3734, www.vcnet.com/measures.