> The 10/3 is fine if your circuit draws less than 30Amps. You should have
2
> lines (or phases as you have called them) and a grounding conductor.
There
> is no neutral in this type of an installation.
There is in this case because the amplifier's 120VAC blower has no 120VAC
tap. Thus, a neutral is still required. See follow-up posting.
> voltage drop should be considered. I would be happy to calclate it for
you
> if you provide the distance and load in ampres.
I should be OK from this persepctive and I also calculated 30-amps. I'm
assuming that the tw-phase breaker should never be rated at more than the
conductor's safe current rating.
> You will not need a neutral if there is not requirement for 120V. in this
> equipment (remember line-neutral = 120V
And there's the fly in the ointment! The blower is the only 120VAC
requirement, thereby requiring a neutral.
73,
-Paul, W9AC
--