You're the second one to ask. It's a GE model # THSASURGE60. It also
has an LED on it so you know it's still working. If the LED goes out,
something inside needs to be replaced.
Barry
John Elsik wrote:
> It appears I need to do more shopping for the AC protection.
> Don't happen to know the GE model number do you?
> Thanks
> John wa5zup
>
>
>
>
>> Date: Wed, 19 Sep 2007 16:52:43 -0400> From: w2up3@verizon.net> To:
>> towertalk@contesting.com> Subject: Re: [TowerTalk] whole house surge
>> protectors> > I had the ICE suppressor on my mains. I had a lightning strike
>> earlier > this summer and the internal parts of the ICE box were fried. The
>> > electrician who inspected the house and did some repairs said it >
>> probably saved us from much more extensive damage (radios, computer, > VCRs,
>> TVs, etc. were dead.) He replaced it with a GE unit that has a > quicker
>> response time and greater Joule rating, and was more expensive> Barry W2UP.>
>> > John Elsik wrote:> > I have been reading this with great interest. I am
>> installing a ground system now. I was going to use an I.C.E 330 for the AC
>> mains (whole house). Would that be adequate? Something is better than
>> nothing. It looks like it is a shunt type also.> > > > John wa5zup> >> >> >>
>> > > >> Date: Wed, 19 Sep 2007 10:34:55 -0700> From: jimlux@earthlink.net>
>> To: towertalk@contesting.com> S
u
>>
> bject: [TowerTalk] whole house surge protectors> > I've been doing a bit of
> browsing> Most of the whole house protectors are shunt mode (which, by the
> way, > can actually cause some problems, making things worse)> > Intermatic
> IG1240RC> Leviton 51120-1> Panamax gpp8005> Siemens various models> > etc.> >
> In any case, a shunt mode suppressor will also suppress transients >
> originating within the house.> > There is a case where they will be of less
> effectiveness.. if you have a > transient induced on the branch circuit
> between the panel and your load, > then the transient propagates both
> directions, and, depending on the > relative lengths of the wire, it will get
> to the load before it gets to > the clamp. Once the clamp goes into effect,
> an inverted transient gets > reflected back, so you can calculate the maximum
> width of the > unsuppressed pulse. (you could use something like> > >> > > 2
> ns/ft as a > propagation speed... so for a 100 ft run, with the transient
> induced > ne
xt
> to the load (or downstream from the load), you get half a > microsecond or
> so before the voltage is clamped.> > > If the transient is induced on a
> branch circuit other than the one your > load is on, the suppressor is
> between the transient source and your > load, so it would clamp the transient
> before it arrives at the load.> > If you put a point of use transient
> suppressor *with a higher voltage* > than the whole house protector, it will
> take care of the half > microsecond impulse before the whole house protector
> kicks in, and won't > have to absorb as much energy.> > FWIW, statistics show
> that most transient damage occurs from transients > originating outside the
> house, typically from a lightning strike or MV > line / LV line fault
> somewhere (MV = 10-30kV, LV = 120,240,480V). That > makes the rise time of
> the transient much slower (it's low pass filtered > by the power line), and
> a> ls> > o makes the whole house protector more > effective.> > In the event
> of a MV/LV sho
rt
> (the only kind of line transient I've had > personal experience with in
> Southern California.. we don't have much > lightning here), you've probably
> got a significant overvoltage that > lasts 8-10 milliseconds or longer (until
> the MV breaker trips or fuse > blows). You'd have to hope that the surge
> suppressor can hold on that > long without blowing its internal fuses. Or,
> ideally, it would short, > and trip your main breaker. Since most of these
> whole house protectors > have energy absorptions in the few kilojoule range,
> I'm not very > sanguine about their ability to protect against this kind of
> fault. > Figure the case of a 14.4kV feeder shorting to the 240V drop into
> your > house (this has actually happened to me). If the series impedance of >
> the feeder, through the drop, into the grounding system, is on the order > of
> an ohm or so, the fault current is around 10-20kA.> > If the surge pr> ot> >
> ector is based on an MOV, the 400V MOV is going to > dissipate about 4-8 MW,
o
> r, 4-8 kJ/millisecond. If it takes a half > cycle for the breaker to
> trip/fuse blow, that's 8 ms, and about 50kJ > (which is why things literally
> explode when this happens).> > A surge protector based on a spark gap, which,
> once it fires, has a much > lower clamping voltage, will dissipate less
> energy in the protector, so > has better survivability.> >
> _______________________________________________> > > >
> _______________________________________________> TowerTalk mailing list>
> TowerTalk@contesting.com>
> http://lists.contesting.com/mailman/listinfo/towertalk> >
> _______________________________________________> >> >> >> >
> _______________________________________________> > TowerTalk mailing list> >
> TowerTalk@contesting.com> >
> http://lists.contesting.com/mailman/listinfo/towertalk> >> >> > > > >
> _______________________________________________> > > >
> _______________________________________________> TowerTalk mailing list>
> TowerTalk@contesting.com> http://lists.contesting.com/mai
lm
> an/listinfo/towertalk
> _______________________________________________
>
>
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk@contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
>
>
>
--